I am working at a plant that has a 6.9kV medium voltage system. The auxiliary transformer is three winding. The primary is 70MVA and the secondary and tertiary are 35MVA in wye configuration with both windings high resistance grounded through a transformer, refer to attached for clarification. I calculated the maximum Ground fault current as 5.67A.
Neutral Grounding Transformer
Vprimary = 4000V
Vsecondary = 240V
Rngr = 1.59 ohms
Transformer Ratio = Vprimary / Vsecondary = 4000V/240V = 16.7
Rprimary resistance = (Transformer Ratio^2)(Rngr^2) = (16.7^2)(1.59^2) = 705 ohms
Ig = Vprimary / Rprimary resistance = 4000V / 705 ohms = 5.67A
5.67A is consistent with a high resistance ground system, but if I use the rule of thumb for the capacitive charging current of 1.5A/MVA the capacitive charging current is approximately 52A. Have I calculated the maximum ground fault current incorrectly?
Note recently a medium voltage motor had a ground fault. All feeders on the medium voltage line-up indicated a ground fault alarms. Once the motor was removed from service all ground fault alarms cleared.
Neutral Grounding Transformer
Vprimary = 4000V
Vsecondary = 240V
Rngr = 1.59 ohms
Transformer Ratio = Vprimary / Vsecondary = 4000V/240V = 16.7
Rprimary resistance = (Transformer Ratio^2)(Rngr^2) = (16.7^2)(1.59^2) = 705 ohms
Ig = Vprimary / Rprimary resistance = 4000V / 705 ohms = 5.67A
5.67A is consistent with a high resistance ground system, but if I use the rule of thumb for the capacitive charging current of 1.5A/MVA the capacitive charging current is approximately 52A. Have I calculated the maximum ground fault current incorrectly?
Note recently a medium voltage motor had a ground fault. All feeders on the medium voltage line-up indicated a ground fault alarms. Once the motor was removed from service all ground fault alarms cleared.