I will briefly outline the situation regarding my question...
-3 Phase 3 wire supply, ~13400V
-1500KVA transformer, brand new, 13800/4160Y/2400, set on 13460V tap
-energized through a recloser (setup to operate as a switch on a three minute timer)... thus all three phases closed at the same time
-overhead line comes down and goes through a very short underground run up through the pad to the primary. All cables are in individual runs.
-NO cables connected on the secondary... purely open connection.
-There is a secondary ground strap running from X0 to ground.
When the transformer was closed in via the recloser, the controller panel read 140A, which seems like a reasonable amount of inrush for a transformer rated at 64A (full load) on the primary. One minute into closing the readout says 160A. Two minutes into closing the readout says 180A. This levels out and stays at 180A until the three minute timer opens the circuit. This current reading has been verified by a separate clamp on meter as well. This is most definately NOT a typical inrush curve. It appears to be loaded somehow... I am assuming some sort of fault. The last critical piece of information is that the secondary ground strap was glowing cherry red through all this. The core is a 5 limb wound core design. This unit has been pulled from location and is currently in our shop. It has passed the insulation resistance test, turn ratio test, insulation power factor test, winding resistance test, energize test, impedance test and induced potential tests with flying colors. There doesn't appear to be anything wrong with the transformer based on the standard battery of tests that we do here. Everyone is stumped. I was hoping one of you guys could shed some light on the potential cause of such a tremendous neutral to ground voltage that it would overheat the ground strap in that fashion. Having a 5-leg core and a delta primary, it would seem that it is redundantly protected from excessive magnetizing imbalances. Let me know what you guys think! Thanks!
-3 Phase 3 wire supply, ~13400V
-1500KVA transformer, brand new, 13800/4160Y/2400, set on 13460V tap
-energized through a recloser (setup to operate as a switch on a three minute timer)... thus all three phases closed at the same time
-overhead line comes down and goes through a very short underground run up through the pad to the primary. All cables are in individual runs.
-NO cables connected on the secondary... purely open connection.
-There is a secondary ground strap running from X0 to ground.
When the transformer was closed in via the recloser, the controller panel read 140A, which seems like a reasonable amount of inrush for a transformer rated at 64A (full load) on the primary. One minute into closing the readout says 160A. Two minutes into closing the readout says 180A. This levels out and stays at 180A until the three minute timer opens the circuit. This current reading has been verified by a separate clamp on meter as well. This is most definately NOT a typical inrush curve. It appears to be loaded somehow... I am assuming some sort of fault. The last critical piece of information is that the secondary ground strap was glowing cherry red through all this. The core is a 5 limb wound core design. This unit has been pulled from location and is currently in our shop. It has passed the insulation resistance test, turn ratio test, insulation power factor test, winding resistance test, energize test, impedance test and induced potential tests with flying colors. There doesn't appear to be anything wrong with the transformer based on the standard battery of tests that we do here. Everyone is stumped. I was hoping one of you guys could shed some light on the potential cause of such a tremendous neutral to ground voltage that it would overheat the ground strap in that fashion. Having a 5-leg core and a delta primary, it would seem that it is redundantly protected from excessive magnetizing imbalances. Let me know what you guys think! Thanks!