2
Hello, When looking at a distribution/transmission system, why are higher voltage lines more dangerous than lower voltage lines? For example when looking at a 4200 V system and a 12470 V system, the current is higher on the 4200 V system which seems like that would be more hazardous. What am I missing? Thank you in advance.
 
Replies continue below

Recommended for you

There is more chance of arc-over with higher voltages.
The higher the voltage the more chance that contact will be fatal.
That being said, the survive-ability of contact with 4200 Volts is almost the same as is contact with 12,470 Volts.
What's a four letter word to describe survival of contact with either voltage?
LUCK


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
That is very true, thank you for your reply.
 
There is complacency at lower voltages that can make them equally dangerous. You'll hear stories of electricians falling over after getting shocked with 120 v and not thinking it a big deal and not seaking medical attention. 120v is scary when your hand is locked onto a live wire and you can't get your hand to let go. Anything 480v and above is like a bomb when it faults and gets treated as such.

------------------------------------------------------------------------------------------
If you can't explain it to a six year old, you don't understand it yourself.
 
The severity of the electric shock it is a combination of the voltage level, current intensity, duration, frequency and point of contacts. The following describes a rough mechanism of electric shock and the importance of the voltage level:
• Under shock exposure over 500V, the skin may cause dielectric breakdown and
• This allows more the current to flow inside the body resulting in tissue damage and may trigger fibrillation of the heart causing cardiac arrest.
• Fibrillation is the most frequent cause of deaths in an electrical accident.
• The importance of the voltage is associated with electrothermal burns is can be explained with Joule’s law:
..>>> [highlight #FCE94F] W =R.I[sup]2[/sup].t = V.I.t = V[sup]2[/sup]/R.t[/highlight] <<<

• Statistics data indicates that shocks above 2,700 V are often fatal and the probability to survive decrease with the voltage level.

Bellow is a link describing a lucky boy that survived 230 kV shock
 
HH and Cucky. I agree with both of you.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 