Good Morning Folks,
NFPA 25, 2001 ed. section 13.5.1.2 requires that sprinkler pressure reducing valves be full flow tested every five years and the data compared to previous test results. To me, full flow testing means testing at system demand, however, the annex material in A13.5.1.2 seems to indicate that a drain valve is adequate to perform the test. Obviously, the drain valve doesn't allow you to measure the flow, so you wouldn't know if you were at "Full flow".
I am thinking a flowmeter, similar to what is used to test 2½" pressure reducing hose valves, should be connected downstream of the sprinkler PRV and connected to the 3" drain riser in a similar manner to the test for hose valves. Shouldn't the flow and residual pressure be measured to make sure the system demand is still available from the sprinkler control PRV??
NFPA 25, 2001 ed. section 13.5.1.2 requires that sprinkler pressure reducing valves be full flow tested every five years and the data compared to previous test results. To me, full flow testing means testing at system demand, however, the annex material in A13.5.1.2 seems to indicate that a drain valve is adequate to perform the test. Obviously, the drain valve doesn't allow you to measure the flow, so you wouldn't know if you were at "Full flow".
I am thinking a flowmeter, similar to what is used to test 2½" pressure reducing hose valves, should be connected downstream of the sprinkler PRV and connected to the 3" drain riser in a similar manner to the test for hose valves. Shouldn't the flow and residual pressure be measured to make sure the system demand is still available from the sprinkler control PRV??