TenPenny
Mechanical
- Nov 7, 2006
- 1,126
Just looking for thoughts based on experience.
We have an end suction ANSI pump, 2x3-8, if that matters. On the test bench, we get performance close to the factory curve, using cold water (15C), suction pressure 4psig.
In the field, the exact same pump with the exact same clearance (nothing was changed), running with 145psig suction pressure and 355F water, the performance is approx. 10% less (as in, let's say at 140 gpm flow rate, on the bench we get 320 ft head; in the field with hot water / high suction press, we get 293 ft).
Obviously, these numbers are adjusted for the SG of the hot water, but is there some other reason that, with the same speed, same impeller, same clearance, and same flow rate, we would get lower head? One would almost think you'd get better performance at the higher temp, as the clearance would tighten up when the pump heated up.
Scratching my head, wondering if it's time for a drink yet.
We have an end suction ANSI pump, 2x3-8, if that matters. On the test bench, we get performance close to the factory curve, using cold water (15C), suction pressure 4psig.
In the field, the exact same pump with the exact same clearance (nothing was changed), running with 145psig suction pressure and 355F water, the performance is approx. 10% less (as in, let's say at 140 gpm flow rate, on the bench we get 320 ft head; in the field with hot water / high suction press, we get 293 ft).
Obviously, these numbers are adjusted for the SG of the hot water, but is there some other reason that, with the same speed, same impeller, same clearance, and same flow rate, we would get lower head? One would almost think you'd get better performance at the higher temp, as the clearance would tighten up when the pump heated up.
Scratching my head, wondering if it's time for a drink yet.