Hillside base level diaphragm

Status
Not open for further replies.

HofOblivion

Structural
Dec 15, 2014
13
I have a project where hillside ordinance is applied. One side of the building is fully day-lighted (T.O. soil and T.O.S. at the same elevation) and the other side is retaining soil up to 8'-0" height. I cannot determine if the I have to assume the base level diaphragm at the roof level (at 10'-0" above the T.O.S.) or at the slab as the building cuts into the (E) soil. Which is the correct way to design this building?
 
Replies continue below

Recommended for you

As you probably have concrete walls on three sides, I would take the base at the 8 foot high floor diaphragm level for forces normal to the slope.

In the other direction parallel to the slope, I would take the base at the slab. You will need wood shear walls at the day lighted wall of the basement.

Mike McCann, PE, SE (WA)


 