steelerr
Electrical
- Jan 25, 2007
- 16
Hi everybody,
I have to perform Ground Bond (GB), Insulation Resistance (IR) and Dielectric Withstand (DW - a.k.a. Hipot) testing on new 3-phase industrial equipment as part of a third-party electrical safety certification.
I will soon purchase an Electrical Safety Tester (EST) to perform these tests (currently I'm renting a unit for learning purposes). Typically, I'll first do the GB test on the equipment, then on the line power circuits I'll perform the IR (Megger) test, then AC hipot, then IR again.
Testing specs as defined by my NRTL:
GB test - 25A for 1 second
IR test - 500Vdc for 1 second
Hipot test - 2 x line voltage + 1000V for 1 second (~2000V)
The hipot testers I've researched allow a minimum current value (say, 0.1mA) to be entered to ensure that the tester is actually connected to the device under test (DUT)- that is, to make sure I don't have an open test lead.
Question 1 - Does this parameter make sense? Shouldn't I expect zero current flow, even at 2000V?
Question 2 - How should I connect my 2-lead hipot tester? Do I connect the HV lead to each winding connection one at a time and the return lead to motor frame? Do I have to read across windings L1-L2, L1-L3, L2-L3? Should L1-L2-L3 be jumpered together and then the reading is taken from that connection to ground?
Thank you.
I have to perform Ground Bond (GB), Insulation Resistance (IR) and Dielectric Withstand (DW - a.k.a. Hipot) testing on new 3-phase industrial equipment as part of a third-party electrical safety certification.
I will soon purchase an Electrical Safety Tester (EST) to perform these tests (currently I'm renting a unit for learning purposes). Typically, I'll first do the GB test on the equipment, then on the line power circuits I'll perform the IR (Megger) test, then AC hipot, then IR again.
Testing specs as defined by my NRTL:
GB test - 25A for 1 second
IR test - 500Vdc for 1 second
Hipot test - 2 x line voltage + 1000V for 1 second (~2000V)
The hipot testers I've researched allow a minimum current value (say, 0.1mA) to be entered to ensure that the tester is actually connected to the device under test (DUT)- that is, to make sure I don't have an open test lead.
Question 1 - Does this parameter make sense? Shouldn't I expect zero current flow, even at 2000V?
Question 2 - How should I connect my 2-lead hipot tester? Do I connect the HV lead to each winding connection one at a time and the return lead to motor frame? Do I have to read across windings L1-L2, L1-L3, L2-L3? Should L1-L2-L3 be jumpered together and then the reading is taken from that connection to ground?
Thank you.