Holdowns with shared post in shear wall

Status
Not open for further replies.

babyfaceeit

Structural
May 25, 2021
1
How do we check the holdown with shared post in corner?
Do we need to account for 30% uplift from another direction?
 
Replies continue below

Recommended for you

Seismic or wind? Can't say for seismic (I'm on the east coast and the seismic loads are never enough to worry about explicitly, I just have to make sure the pieces are there), but for wind ASCE 7 provides several load cases that involve multi-directional and torsional responses. For each load case, you can determine the shear in each shear wall and the reaction at the ends. Sum the uplifts at the shared post.
 
I check for the worst case hold down at the corner in each direction and use that holddown at the corner.

I do not combine directions, only use the worst case.

Mike McCann, PE, SE (WA, HI)


 
For Wind - not that I know of. You can to be conservative I guess.

For Seismic - depending on the Seismic Design Category, if it's D to F, then you have to account for the Orthogonal Effect of that holddown (because it is considered part of a column or wall that forms part of 2 or more intersecting SFRSs). Which means you are on the right track. Basically you design for the max of:
1) 100% of the direction you are analyzing PLUS 30% of the other orthogonal direction
2) 100% of the other orthogonal direction PLUS 30% of the direction you are analyzing

Sauce (a slang for source): ASCE 7-16 Section 12.5
 