You will notice the shear is huge from the center C1 to the secondary beam framing into the middle of the right girder. Stirrup spacing should have been uniform 100mm or 4 inches. But the problem is we followed the 10 @ 100, 8 @ 150, rest 200. This means the 10 - 100mm spacing only reaches up to 3/4 or less of the big shear span (only 3/4 up to where the secondary frame into the right girder). If we used uniform 100mm the entire girder, no problem, but we didn't. Not only that. We didn't use 60 ksi (no stock so we requested 40ksi after approval) and we didn't put the middle leg. This is why there are 3 misses and that is why the designer recommends shear strengthening but he hasn't done CRFP before and the journals gave me concern.
The reason for adverse effect of steel stirrup and CRFP is because the debonding is not uniform, so the parts where debonding has not taken place, the diagonal crack is pinned, the one where debonding has taken place, the diagonal crack opens. After the CRFP snaps at its ultimate load, all the stirrups with no uniform yield would react suddenly. All this concerns only occurs because of debonding. If there is no debonding before the CFRP snaps, there is no problem because you will reach the beam shear limit before it fails if no debonding occurs.
Now in the steel tendons scenerio at sides with plates underneath. There is no debonding process. So if the steel tendons hold. Then it can be a solution. Can the bolts and nuts hold, or welding or any means to secure it?