My last question especially for moamen2020, hokie66, Ingenuity, Baretired, etc.
Below is the stirrup spacings of the 6 meter girder beam.
From face to face of columns, closed stirrups spacing starts at 1 stirrup at 50mm from column, then 10 stirrups at 100mm (4") spacing, 8 stirrups at 150mm
(6)" spacing and middle at 200mm (8") spacing. The beam is 500mm in depth, 300mm in width, there are 3 200mm (8") spacing stirrups at center (see picture) where 6-meter secondary beams on both sides framed into it. My concern is the contractor move one of the midpsan stirrup closer resulting it in forming 200mm, 100mm, 300mm spacings (see picture)..
Since the depth of the beam from tension bars to compression is 460mm.. half of it is 230mm... so one of the beam spacings at center didn't satisfy D/2 or 460/2=230mm because it has one 300mm spacing.
The following shows the shear and moment diagram at that location at 1.2 DL + 1.6 LL.
The concrete section + 300mm spacing stirrup has shear capacity V(c+s) more than the Vu (factored ultimate load).. which fulfills the spacing requirement but it doesn't satisfy D/2. According to the designer team and head, no problem with it since shear at midspan is not much. But I still have worry because it doesn't satisfy D/2. I told him what if diagonal cracks form there. He said he hasn't seen it happened. Now the reason I asked this is because I can have the 2 inches floor topping removed and change it to mere 3/4" topping to remove some Superimposed dead load to get even bigger margin.. the designer team and head said I can decide whether to do it or not. Isn't not satisfying D/2 in one of the stirrup a problem especially it is on midspan?