jjmoore73
Mechanical
- Apr 13, 2011
- 30
I have a single story 100,000 sq. ft. concrete fitness center project. It will have automatic sprinklers and a Class I Standpipe system with 13 2.5" hose valve locations.
According to 7.10.1.1.1 the minimum flow rate should be 500gpm at the most remote location through two 2.5" outlets at one location, then 250gpm at the next two remote hose connections in accordance with 7.10.1.2.
Based on 7.10.1.1.2, AHJ said I only need to flow 750gpm total for this project because it is a horizontal standpipe. (250gpm for 3 different hose valves) What say you?
Based on 7.10.1.1.3, leads me to believe I should not only have 1000gpm total, but 500gpm should be at the two most remote locations.
Based on 7.10.1.2.2 says I need to calculate 250gpm at the three hydraulically most remote hose connections on the standpipe AND at the topmost outlet of each of the other standpipes. Say what?
I need some help determining how many and which hose valves need to be calculated. Based on the attached plan, I am thinking 250GPM at F,G,H,L. I am also showing where I am planning on the isolation valves. If I need to calculate 500gpm at one location, do I need to provide 2 hose valves at that location?
Thanks - J
J. Moore
NICET III - Water Based
According to 7.10.1.1.1 the minimum flow rate should be 500gpm at the most remote location through two 2.5" outlets at one location, then 250gpm at the next two remote hose connections in accordance with 7.10.1.2.
Based on 7.10.1.1.2, AHJ said I only need to flow 750gpm total for this project because it is a horizontal standpipe. (250gpm for 3 different hose valves) What say you?
Based on 7.10.1.1.3, leads me to believe I should not only have 1000gpm total, but 500gpm should be at the two most remote locations.
Based on 7.10.1.2.2 says I need to calculate 250gpm at the three hydraulically most remote hose connections on the standpipe AND at the topmost outlet of each of the other standpipes. Say what?
I need some help determining how many and which hose valves need to be calculated. Based on the attached plan, I am thinking 250GPM at F,G,H,L. I am also showing where I am planning on the isolation valves. If I need to calculate 500gpm at one location, do I need to provide 2 hose valves at that location?
Thanks - J
J. Moore
NICET III - Water Based