Hose estation on foam sprinkler cross-feed main?

Status
Not open for further replies.

DavidCR

Mechanical
Jan 10, 2002
355
Is it allowed (per NFPA 13) to connect a hose cabinet (hose station, class III) to a cross main or feed main of a foam sprinkler system that is feed by water foam solution (AFFF-3%)?.



 
Replies continue below

Recommended for you

I see no prohibition. I wouldn't do it, but its not prohibited.

The reason I am against this design is your probably protecting a high-challenge commodity and you want to utilize the foam-water solution to control the fire involving the hose stream. If its flammable liquids, the thermal flux will be so great the plant operator will run like a screaming child, drop and leave the nozzle open, and all of the foam lost through the hose nozzle will be lost. The sprinkler system is more effective in applying the foam/water solution.
 
It is a process oil pump room. The contractor found complicated to get an additional water pipe from the hydrant mains to feed the hose station, so he took it from the sprinkler system.

Per local regulations we need both sprinklers and hose in the area.

We wanted to force him to get it from the water pipes, but it seems there is no point in the contract to make it, and I cannot find the issue on the NFPA.

The foam sprinklers are in a grid system, the hose is connected on one of the sides of the grid mains.

I was looking for something like an inconvenience on "stealing" water from the sprinkler on the middle of the grid, or something similar.

I agree with you I don´t like it.
 
Is there an adequate foam supply to still have the required duration if one uses that hose? You may only have a 10 minute supply for the sprinklers, but it may not include flow coming from that hose station.

Travis Mack
MFP Design, LLC
 
Yes. There is "Firedos" european hydraulic proportioner that provides foam for other bigger risks with enough capacity.
 