pipesnpumps
Mechanical
- Dec 4, 2002
- 316
What are the requirements for design flow for a combined system standpipe?
Let's say I am designing for NFPA 13 Ordinary 2, I read that the inside hose would be 100 gpm and outside would be 150 gpm (total 250 gpm inside/outside).. But the purpose of a 100 gpm hose (1-1/2") would be for first-aid fire fighting and clean up, not fighting a fire..
Then NFPA 14 requires four 2-1/2" hoses (1000 gpm total), but without any sprinklers flowing.
So does NFPA 13 or NFPA 14 not address the situation of design sprinklers flowing at the same time as 2-1/2" attack hoses?
I don't understand the logic of designing either for
a) sprinklers + a clean-up hose, or
b) four 2-1/2" attack hoses, but no sprinklers operating..
Am I just imagining that firefighers would want to leave the sprinklers operating and still hook-up to hoses? If so, the system would not be designed to accomodate both the hoses and a design fire area.
If anyone can shed some light, I would appreciate it!
Let's say I am designing for NFPA 13 Ordinary 2, I read that the inside hose would be 100 gpm and outside would be 150 gpm (total 250 gpm inside/outside).. But the purpose of a 100 gpm hose (1-1/2") would be for first-aid fire fighting and clean up, not fighting a fire..
Then NFPA 14 requires four 2-1/2" hoses (1000 gpm total), but without any sprinklers flowing.
So does NFPA 13 or NFPA 14 not address the situation of design sprinklers flowing at the same time as 2-1/2" attack hoses?
I don't understand the logic of designing either for
a) sprinklers + a clean-up hose, or
b) four 2-1/2" attack hoses, but no sprinklers operating..
Am I just imagining that firefighers would want to leave the sprinklers operating and still hook-up to hoses? If so, the system would not be designed to accomodate both the hoses and a design fire area.
If anyone can shed some light, I would appreciate it!