Mechanical
Sep 19, 2010
34
follow engineers
who co could provide insight on the selection of boiler and HX kw capacity and the Storage volume of vessel ( the balance point between heat generation & storage volume)
the application is an industrial application requiring 85°C d hot water heat from 10°C
heat source will be fire tube superheated water boiler (not steam)
average drawdown of water =1.5 kg/s
ASHRAE have Recovery/ vs heating Capacity curves for domestic applications ( i cant find similar for industrial applications)
any hints & reference will be appreciated
 
Replies continue below

Recommended for you

to clarify how : how to find the balance between vessel storage size and heating capacity?
any rules of thumbs or guidelines available on the subject?
 
My first rule of thumb would be find an experienced Process Plant/Thermal Engineer ...

- Develop a realistic Block Flow/PID drawing

- Model your proposed system in a Heat Balance software package (possibly one that has the desired ASHRAE curves)

- Run various cases and decide upon the best solution

MJCronin
Sr. Process Engineer
 
This should fix you up. I developed it for storage tank water heaters. Units are imperial. The easiest way to use it is to put it in a spreadsheet. There, you can play with the variables and see what happens. Heat input to tank is net heat, assuming some efficiency of the boiler.
 
 https://files.engineering.com/getfile.aspx?folder=408c3029-787e-4386-a76f-02864a7af237&file=STWH.pdf