Hi All, I'm new here and have two questions. My first question is how do you size a freeze pump for hot water pre-heat application? Second question is how do you control it?
 
Replies continue below

Recommended for you

You have to determine how many GPM is required through the coil. You can use this: GPM = 2.16(cfm/1000)(air temp. rise*F/water temp. drop *F)Then you can use an eletric controller with a remote bulb. The formula is derived from ASHRAE guide for ACHVR.
Roger
 
Thanks Roger, I have done the calc for the coil GPM, but is the pump typically sized for the full coil flow rate. Teh second question was more of a sequence question. Some say run it all the time, others say run it based on Outdoor Temp.
 
I've seen this start and run at and below 40°F OA temp.
 
I like to run it based on OSA temp I see no need to run it all the time if OSA gets above 40*f and yes its sized for full flow.
 