My point is that if the nominal voltage (net voltage)decreases and the power drew by the load is constant the current will increase. And some meters use this current, as the only parameter, to move a wheel (using the Eddy Current and the electromagnetic force) which is the motor of the clock that shows the reading.
Industrial meters use PT and CT, and this values are passed to the meter and then the energy is determined.
Power(W)= V x I x cos &
Energy(Wh) = V x I x cos & x h
The meter has to register V and I to determined the exact energy drew. And using only the current, like the old residential meter, it will create a wrong reading. I know that the voltage has to stay close to the nominal value (240/120 V), but if it change to 100 V some load will work with this value and will draw more current. The meter using only the current like parameter will register more energy.