Hi:
I am not a protection guy. I know if the line series compensations go beyond 50% the distance relay may mis-operate due to the possible negative impedance (Or out of the cycle).
Differential relay is preferred. However, our 500kV system uses microwave not fiber. So one of my friends told me differential relay can not be applied by micro wave. Is it true?
I read some books it said phase comparison relay can also be applied .For microwave communication, can phase relay be applied.
Another question is that, our P&C guys said if the series cap can be located at exactly the mid point of the line. then they may make 65% series compensation work based on distance relay. But due to the Geo. limits, mid point location will be highly unlikely the case. therefore, we've been told the compensation level can not go beyond 50%.
I don't know exactly why the location becomes a very important factor?
I knew back to 1960-1970s US installed a lot of series compensation more than 70%. Don't know exactly how they apply the protection scheme and which type of communication they used at that time.
I know we can take the risks by relaying on series cap short out right after the fault by MOVs. But I would like to learn if we don' not relay on MOVs what should be the right thing to do
Hope any experts who did 500kV line protection with more than 60% series compensation provide some directions.
Thanks!
I am not a protection guy. I know if the line series compensations go beyond 50% the distance relay may mis-operate due to the possible negative impedance (Or out of the cycle).
Differential relay is preferred. However, our 500kV system uses microwave not fiber. So one of my friends told me differential relay can not be applied by micro wave. Is it true?
I read some books it said phase comparison relay can also be applied .For microwave communication, can phase relay be applied.
Another question is that, our P&C guys said if the series cap can be located at exactly the mid point of the line. then they may make 65% series compensation work based on distance relay. But due to the Geo. limits, mid point location will be highly unlikely the case. therefore, we've been told the compensation level can not go beyond 50%.
I don't know exactly why the location becomes a very important factor?
I knew back to 1960-1970s US installed a lot of series compensation more than 70%. Don't know exactly how they apply the protection scheme and which type of communication they used at that time.
I know we can take the risks by relaying on series cap short out right after the fault by MOVs. But I would like to learn if we don' not relay on MOVs what should be the right thing to do
Hope any experts who did 500kV line protection with more than 60% series compensation provide some directions.
Thanks!