Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

How do I calculate voltage drop in a 400Hz system?

Status
Not open for further replies.

toro45

Electrical
Dec 16, 2003
17
0
0
US
I am looking for helpful information on performing voltage drop calculation on a 400Hz system.
Any pointers will be greatly appreciated.
 
Replies continue below

Recommended for you

There should be no difference as long as you use appropriate R and X for the higher frequency. R will be higher because of skin effect. X will be higher because it is proportional to the frequency (X = 2·pi·f·L). There is also a skin effect for X as well as the proportionality.
 
Alternatively you can utilize software for power flow like ETAP. Change the project frequency to 400 Hz and when you select 50/60Hz cables from the library, ETAP automatically calculates the new impedance based on 400 Hz. I have seen this application used for shipboard power systems.
 
Toro, Is this for a 400Hz aircraft power distribution system? If so I've got loads of info. If not, I'll wait for more posts so as not to waste time.
 