bacon4life
Electrical
- Feb 4, 2004
- 1,526
General question: For a typical +/- 10% LTC, what is the expected variation in fault current.
Detailed question:
I am attempting to calculate faults when using a transformer with the off nominal taps, but I haven't found a good example to follow yet. When calculating the per unit impedance of a tranformer with taps, do you use the same voltage & MVA base, or do you use the new voltage and the same MVA base?
As an example, if I have a 4 kVA, 3 phase, 230 to 115 tranformer with 10 primary turns at 0.1 ohm per turn and 20 secondary turns at 0.05 ohms per turn, then the Zpu is 0.094.
1: If I add 1 primary turn and use the same MVA and voltage base, the per unit impedance would be 0.106, a change of 12%.
2: If I add 1 primary turn and instead use the same MVA and use 207 for the voltage base, the per unit impedance would jump up to 0.13, a change of 38%.
3: Since I neither of these seemed quite right, I also tried calculating the fault current with real units as follows:
Nominal
Zprimary= 1.0 ohm
Zsecondary 1.0 ohm
Ztotalrefered to high side = 1.25 ohm = 1.0 + 1.0* (10/20)^2
Iprimary = 106A= 230/1.25/1.73
Isecondary = 212A = 106A * 20/10
One extra highside winding:
Zprimary= 1.1 ohm
Zsecondary 1.0 ohm
Ztotalrefered to high side = 1.4025 ohm = 1.1 + 1.0* (11/20)^2
Iprimary = 94.7A= 230/1.4025/1.73
Isecondary = 172A = 94.7A * 20/11
A change of 26%
Detailed question:
I am attempting to calculate faults when using a transformer with the off nominal taps, but I haven't found a good example to follow yet. When calculating the per unit impedance of a tranformer with taps, do you use the same voltage & MVA base, or do you use the new voltage and the same MVA base?
As an example, if I have a 4 kVA, 3 phase, 230 to 115 tranformer with 10 primary turns at 0.1 ohm per turn and 20 secondary turns at 0.05 ohms per turn, then the Zpu is 0.094.
1: If I add 1 primary turn and use the same MVA and voltage base, the per unit impedance would be 0.106, a change of 12%.
2: If I add 1 primary turn and instead use the same MVA and use 207 for the voltage base, the per unit impedance would jump up to 0.13, a change of 38%.
3: Since I neither of these seemed quite right, I also tried calculating the fault current with real units as follows:
Nominal
Zprimary= 1.0 ohm
Zsecondary 1.0 ohm
Ztotalrefered to high side = 1.25 ohm = 1.0 + 1.0* (10/20)^2
Iprimary = 106A= 230/1.25/1.73
Isecondary = 212A = 106A * 20/10
One extra highside winding:
Zprimary= 1.1 ohm
Zsecondary 1.0 ohm
Ztotalrefered to high side = 1.4025 ohm = 1.1 + 1.0* (11/20)^2
Iprimary = 94.7A= 230/1.4025/1.73
Isecondary = 172A = 94.7A * 20/11
A change of 26%