I was called to try and figure out why a contactor in an elevator panel keeps burning out. This was the second time it happened. Although I suspect the contactor was under-rated I want to make sure. I got this on the partially burned nameplate of the sprecher+schuh brand contactor:
AC-1...
AC-3
V 415 500 610
kW 25 31 32
600Vac, 72A
120V, 60Hz
110V, 50Hz
Can you please enlighten me on the conventions used so I can interpret contactor nameplate ratings correctly, especially what AC-1 and AC-3 means?
What is the relation of the 600Vac, 72A to the V and Kw rating under "AC-3?"
i=32kw/(1.732x610)
i=30.2A
Thanks!