Thinking back to GE pilot wire relays I worked with in the past, you need ONE pair of relays.
I worked on systems for in-plant industrial distribution at the 15 kV level where multiple conductors per phase were the norm. I also worked with them in an transmission-distribution system where we protected several short-length 69 kV transmission lines between close-together substation.
A CT for each phase at each end feeds into its corresponding relay. There, conversion takes place to the actual signal-level current that passes over the pilot wire for comparison from end to end, basically a long-reach differential scheme. The comparison current is an AC waveform. On the old GE scheme, a DC signal was piggy-backed onto the pilot wire and provided integrity check functions. If the pilot wire failed, the relays then reverted to a gross-order overcurrent function.
They're slowly (like much in the utility biz) being phases out in favor of smart relays which can replicate that function and much more with modern communications.
old field guy