Hi folks,
We have just completed an independant & detailed evaluation of one of the leading energy saver products and would like to present our findings to you.
- At 0% motor loading, a saving of less than 18% was achieved.
- At 25% motor loading, a saving of less than 3% was achieved.
- At 50% motor loading, a saving of less than 1% was achieved.
- At 75% motor loading, there was no energy saving to speak of.
- At 100% motor loading there was no energy saving, as you would expect.
As the above-mentioned results were achieved with a very small and inherently inefficient motor, we would expect savings potential to reduce as one moves up the kW spectrum ie where motors are generally far more efficient.
Note: The above results have not been posted in an attempt to dispute any claims made by manufacturers of this type of equipment and/or information presented by others who may have conducted similar performance appraisals. They have simply been posted to highlight that the overall performance one can expect from such devices is very much subject to variables (eg. motor design, efficiency, kW rating, number of poles & shaft loading) that are outside of our (and the product manufacturers) control. Identification of suitable applications prior to purchase is therefore strongly reccommended.
Regards,
GGOSS
We have just completed an independant & detailed evaluation of one of the leading energy saver products and would like to present our findings to you.
- At 0% motor loading, a saving of less than 18% was achieved.
- At 25% motor loading, a saving of less than 3% was achieved.
- At 50% motor loading, a saving of less than 1% was achieved.
- At 75% motor loading, there was no energy saving to speak of.
- At 100% motor loading there was no energy saving, as you would expect.
As the above-mentioned results were achieved with a very small and inherently inefficient motor, we would expect savings potential to reduce as one moves up the kW spectrum ie where motors are generally far more efficient.
Note: The above results have not been posted in an attempt to dispute any claims made by manufacturers of this type of equipment and/or information presented by others who may have conducted similar performance appraisals. They have simply been posted to highlight that the overall performance one can expect from such devices is very much subject to variables (eg. motor design, efficiency, kW rating, number of poles & shaft loading) that are outside of our (and the product manufacturers) control. Identification of suitable applications prior to purchase is therefore strongly reccommended.
Regards,
GGOSS