How much fault contribution from a converter?

Status
Not open for further replies.

pwrtran

Electrical
Apr 25, 2008
341
Hi folks

I like to get some help on this - does anyone have some idea on how to calculate the fault contribution from a photovoltaic-converter generation that is connected to a distribution system?

Thanks!
 
Replies continue below

Recommended for you

Generally it's very limited because the inverter shuts itself down.
 
Hi dpc

Couple more questions based on your comments:

1) does the converter shut down by protection or by the nature of attenuation?
2) what's typical momentary short circuit current in pu compared to its FLC?
3) what is a division point of over load and over current in terms of %

Thanks
 
Many inverters have a maximum current output that is only 1.1 to 1.2 times full load. Apply a short circuit to the output of the inverter and it will shut down on undervoltage, not overcurrent.
 
As David Beach said, these things cannot put out much fault current even when they try. One big problem with UPS inverters is that they cannot clear a downstream molded case circuit breaker of any size without transferring the load to the mains via a static switch.

The inverter protection circuitry shuts it down on undervoltage.
 