Hello,
I need help resolving the heat balance equations for dryer. My process requires 500 CFM of at 200 Deg F. Ambient air at 75 deg F is being heated in a steam coil injected with 60 PSIG sat steam. Saturated condensate is returned at 252 Deg F. I need to calculate the amount of steam the dryer needs. My calculations yield approx 71.4 8Lbs/hr of stem but I feel I am missing something - intuitively should be a bit more.
Any help would be greatly appreciated with equation and yield.
My calculation was:
cfmx1.08xDelta T/Hfg at = 500x1.08x125/943 (Latent heat at 252 DEg F)
Thanks and regards
Janus
I need help resolving the heat balance equations for dryer. My process requires 500 CFM of at 200 Deg F. Ambient air at 75 deg F is being heated in a steam coil injected with 60 PSIG sat steam. Saturated condensate is returned at 252 Deg F. I need to calculate the amount of steam the dryer needs. My calculations yield approx 71.4 8Lbs/hr of stem but I feel I am missing something - intuitively should be a bit more.
Any help would be greatly appreciated with equation and yield.
My calculation was:
cfmx1.08xDelta T/Hfg at = 500x1.08x125/943 (Latent heat at 252 DEg F)
Thanks and regards
Janus