HouseBoy
Structural
- Nov 21, 2005
- 464
I have a stone veneer that will bear on the concrete ledge at the top of the foundation wall with 1" overhanging.
The stone is a "cut stone" so very uniform thickness of 3" and 4" to create some surface texture. All stone will bear 3" on the concrete (i.e. some will project 1" and some 0" beyond the face of the concrete ledge.
The way that I am looking at it is that bearing contact for the veneer will be within the middle 1/3 of the stone so..... there should be no net tension on the bearing.
Veneer anchors will be with Wire-Bond #1004 type III screw on veneer anchor with #1100 triangular ties.
Any technical issues with the amount of overhang?
Yes I would prefer to have less overhang but adding a plate or angle at the bearing ledge will be problematic and half of the stones will be the 3" thickness so, seems like the CG will be sufficiently behind the edge of the bearing.
The stone is a "cut stone" so very uniform thickness of 3" and 4" to create some surface texture. All stone will bear 3" on the concrete (i.e. some will project 1" and some 0" beyond the face of the concrete ledge.
The way that I am looking at it is that bearing contact for the veneer will be within the middle 1/3 of the stone so..... there should be no net tension on the bearing.
Veneer anchors will be with Wire-Bond #1004 type III screw on veneer anchor with #1100 triangular ties.
Any technical issues with the amount of overhang?
Yes I would prefer to have less overhang but adding a plate or angle at the bearing ledge will be problematic and half of the stones will be the 3" thickness so, seems like the CG will be sufficiently behind the edge of the bearing.