How to calculate solar heat load on a roof?

Status
Not open for further replies.

sabotage

Mechanical
Dec 29, 2006
28
0
0
US
I am determining the amount of air required to cool a outdoor space with only fans, so the indoor and ambient temperatures will be very similar. For my purposes the roof load from the sun will be the only heat conducted to the space.

The only method I have found to determine solar load is the CLTD (Cooling Load Temperature Difference) method with Q = U * A * CLTD, although I am not sure it is appropriate for ONLY solar loads. Is there another method to determine solar loads suitable for manual calculations?

 
Replies continue below

Recommended for you

Could you define the "space" a bit better.

Is it only an area? Is there a canopy or other shade?

If you have no walls and the room under the roof is cooler than outside you have no conduction.
 
IRstuff: You're correct that I did not perform any sort of search, I will definitely do one in addition to this thread. However, I would also appreciate any help you would have to offer on this subject.

MintJulep: It is a single story building with only one room and no windows. A standard construction of four walls and a roof with no shading.
 
I just reread my first post and realized that it was causing the confusion, it is not an 'outdoor' space as I stated. It is just a building located outdoors, which now that I've typed it out sounds extremely redundant.

I hope this clears up any confusion I've caused. If it helps the building in question is a simple maintenance garage for vehicles with a flat built up roof.
 
Let me redo that equation:
1120W/m^2 in * absorptivity = passive convection up + radiation up + conduction down.

The interior surface then has:
conduction down = forced convection + radiation down

Given the boundary conditions, there will be a T.rooftop and T.ceiling that balances all the heat flows.

TTFN

FAQ731-376
Chinese prisoner wins Nobel Peace Prize
 
IRstuff: During my search on the board I've seen you use the figure 1120W/m^2 in other replies, and you mention you took it from some MIL spec, is there an ASHRAE equivalent? I understand this is the peak solar radiation for something like 1% of the year?

MintJulep: Yes, that would just be ridiculous then! Also, thank you for the confirmation that the CLTD calculation is appropriate. I am using the 1997 ASHRAE Fundamentals (which was the last year CLTD tables were produced in ASHRAE) for guidance but I will also check out your link. I'm assuming you're not aware of any other method for this calculation (beside the one IRstuff has posted)?
 