Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

How to calculate the water delivery time in dry standpipe system

Status
Not open for further replies.

Kcann88

Mechanical
Jul 2, 2014
3
I need to provide a calculation showing the water delivery time in a dry standpipe system for a marina dock. Does anyone know what the calculation is? I cannot find anything on this topic anywhere.

Thanks
 
Replies continue below

Recommended for you

Is it an automatic or manual standpipe? Second question: why? I can't recall any instance where NFPA 14 requires a water delivery time.
 
Manual. The town is requiring it for some reason.
 
NFPA 14-2010 defines a manual dry standpipe system as "A standpipe system with no permanently attached water supply that relies exclusively on the fire department connection to supply the system demand." No matter what mathematical method you elect, the answer will always be "it depends what fire truck is pumping into the other end".

Were it an automatic dry standpipe system in excess of 750 gal, NFPA 14 5.2.1.2.2 would require that water be delivered to the most remote hose connection within 3 minutes.

Perhaps the AHJ is confusing manual and automatic standpipes?

R M Arsenault Engineering Inc.
 
If the system is built, test it by flowing the inspector test connection placed at the most remote point of the sprinkler system. Insurance companies have requirements so contact them, perhaps their specialist can help.
 
Its not built its in design. Thanks for the help I will check out the insurance thing
 