Hello everybody,
a customer of mine has asked me a clear explaination on how to connect a 6 cable Star Delta motor for a direct start-up.

I know how to do it practically but I look for some clear instructions (with drawings?) that might maybe already be found on the net.

Can you give me a hint?

Thank you.
A.
 
Replies continue below

Recommended for you

Your motor should have a diagram in it showing the connection patterns for Star and again for Delta. Use only the delta connection pattern. Motor manufacturers sometime bvary with regards to terminal marking etc. so it is best to use the information that came with your motor. If it is lost, contact the manufacturer.

"Venditori de oleum-vipera non vigere excordis populi"


 
A.

This is easily solved, just use three copper links or crimped single core cables (large enough to carry the phase current = F.L.I / 1.732) to link out the three sets of motor terminals.

I.E connect:-

U1 to V2
V1 to W2
W1 to U2

Hope this helps?

Alan
 
Thank you all for the help!
Indeed we DO produce motors... I had just to structure some PPT instructions for my friend...
Well... it took me some time but he thanked me so... I think your help was ok!
Thank you again.
A.
 