tlsps
Electrical
- May 23, 2010
- 6
We replaced across the line hydronic pump starters with VFD's. The pumps are on the 6th floor of a 6 story office building, pumps down the riser with a return running to the basement and a reverse return runs back to the pump inlet on 6th. We installed a DP sensor at 2nd floor ceiling (2/3 down vertically from pump) and connected between the supply line and the common return. The pressure differential was at 12 psi at 100%, and went down to 10psi at 80%. As we reduced the VFD below 80% little happened to the pressure difference. We tried connecting to the reverse return and same thing. We tried a combination of opening and closing in various percentages of each of the return lines (we hooked up with a tee and valves so we could try all combinations). The reverse return has self balancing characteristics so may be the problem. We really wanted to control down to at least 15%, but no luck.
Does anyone know how we can control the VFD with this 3 pipe vertical riser system with the pump at the top of the 6 story riser?