760106
Mechanical
- Jul 28, 2003
- 9
In one project,we used one fire water pump with capacity about 350m3/h, 120mlc, the power rate of the motor is 220Kw,the discharge pipe diameter is DN300. The check valve between the pump is about 2meter. The pump is under the water line, so the piping between the check valve is full of water. The pressure in the downstream piping of the check valve is always remain 12Bar. We need the fire water pump start with the discharege valve of the pump fully opened and all the fire hydrant and the spray are closed, but in fact the pump can not be started. Beacaue the motor is a little small and the starting time is too long.We have tried many times,and every time the swith board was disconnected. so very time, we have to close the discharge valve to start the pump, and then open it.
In final, we installed a orifice plate in the outlet of the pump, and this time, the pump can be started with the discharge valve fully opened.
Question 1:
Can anybody tell me what the difference between the pump start without the orifice plate and the pump start with the orifice plate?
The piping system is full of water,all the hydrant is close. when the pump start, it is also like the close discharge valve to start, but why it can not be started?
Question 2:
for the fire water pump start with the discharge valve fully open, how much power rate should be fit for the pump?
Is there any empirical equation to calculate?
In final, we installed a orifice plate in the outlet of the pump, and this time, the pump can be started with the discharge valve fully opened.
Question 1:
Can anybody tell me what the difference between the pump start without the orifice plate and the pump start with the orifice plate?
The piping system is full of water,all the hydrant is close. when the pump start, it is also like the close discharge valve to start, but why it can not be started?
Question 2:
for the fire water pump start with the discharge valve fully open, how much power rate should be fit for the pump?
Is there any empirical equation to calculate?