I am working on an interaction diagram for a circular, tied concrete column in accordance with CRSI's Design Guide for Reinforced Concrete Columns. For pure bending, CRSI states that there is no closed-form solution to determine the depth of the neutral axis and that a trial-and-error approach must be used. However, they do not go over the approach.

Is anyone able to help here?

Thanks!
 
Replies continue below

Recommended for you

I'd think it the same as with rectangular columns:

1) Assume a NA location.
2) Work out P & M for that.
3) Adjust a NA location.
4) Construct a PM diagram.

 
Just clued in that you're looking for the pure moment case. Pretty much the same though:

1) Assume NA location.
2) Calculate P & M for that.
3) If P isn't zero, move the NA around until it is.

From an algorithmic perspective, you could use your starter NA as the depth it would be if it were a rectangular section of the same width and shift downwards from there. Somewhat less brute force-ish.

 
The procedure is like a rectangular section. (And it is a trial and error procedure.)

Figuring the area of the compression zone (and it's centroid) is a challenge by itself. In Wang & Salmon's Reinforced Concrete design text (p. 504-505 in the 6th edition), they've got a some design aides to that end.
 
Should be able to plug the calculations into an Excel sheet and do a goal seek to find the correct neutral axis depth.
 
My RC Design Functions spreadsheet has a function for elastic analysis of a circular section, with or without axial load:

For strength analysis it is actually easier because you only have to equalise the internal and applied forces, but I haven't got round to doing a function for a circular section yet.

You can use my Beam Design Functions spreadsheet, but you need to enter the concrete as a series of trapezoidal layers, and enter the depth from the top for each pair of reinforcing bars:

The spreadsheets include an iterative solver function that is much faster than using Excel goal-seek, and is easy to automate with VBA.

Doug Jenkins
Interactive Design Services
 