How do I determine new capacity for heat exchanger with plugged tubes. Will the design "U" stay the same if over half the tubes are plugged?
I have a 31 tube, U-tube, Brown Fin tube Exchange that we have 18 tubes that are plugged with process material. We have no known tube leaks. Kerosine/olefin on the tube side and Hot Oil (Therminol) on the shell side.
Having 18 tubes plugged means that the original design:
velocity has gone up from 2.24ft/sec to 5.35 ft/sec.
pressure drop has gone up from 0.63psig to 1.4psig
effective heat transfer area has gone down from 204 ft2 to 85.7 ft2.
Original U is 57.3 BTU/(hr * ft2 * °F), but I think the U should change because I've increased the velocity (U decreases)and effectively increased the bulk shell side temperature (U increases)... but I don't know if these cancel out.
I found some correlation graphs in Rules of Thumbs for Chemical Engineers, but do not know the h for the tube and shell side, and do not know how to back calculate it from the known information...
At a minimum, just from heat transfer area, I'm probably at less than 42% of the old capacity, but I'm not sure if the additional heat now available in the bulk shell side hot oil offsets the velocity increase in the process fluid.
We did not plug the tubes with plugs, and no we're not planning on running this way forever, only long enough to get the unit back up and making what production I can while we get a new bundle built and can shut this unit down and install it. Then we can cut some plugged tubes in the original exchanger and figure out what we plugged them with. Tried a 10K blasting unit and wand is stopped 14-16 inches down tube. No process material removed at all. Normal plugging is a waxy pudding to clay consistancy, not concrete. Exchanger spec sheet and analysis, as well as tube map are attached.
Thanks,
TBell
I have a 31 tube, U-tube, Brown Fin tube Exchange that we have 18 tubes that are plugged with process material. We have no known tube leaks. Kerosine/olefin on the tube side and Hot Oil (Therminol) on the shell side.
Having 18 tubes plugged means that the original design:
velocity has gone up from 2.24ft/sec to 5.35 ft/sec.
pressure drop has gone up from 0.63psig to 1.4psig
effective heat transfer area has gone down from 204 ft2 to 85.7 ft2.
Original U is 57.3 BTU/(hr * ft2 * °F), but I think the U should change because I've increased the velocity (U decreases)and effectively increased the bulk shell side temperature (U increases)... but I don't know if these cancel out.
I found some correlation graphs in Rules of Thumbs for Chemical Engineers, but do not know the h for the tube and shell side, and do not know how to back calculate it from the known information...
At a minimum, just from heat transfer area, I'm probably at less than 42% of the old capacity, but I'm not sure if the additional heat now available in the bulk shell side hot oil offsets the velocity increase in the process fluid.
We did not plug the tubes with plugs, and no we're not planning on running this way forever, only long enough to get the unit back up and making what production I can while we get a new bundle built and can shut this unit down and install it. Then we can cut some plugged tubes in the original exchanger and figure out what we plugged them with. Tried a 10K blasting unit and wand is stopped 14-16 inches down tube. No process material removed at all. Normal plugging is a waxy pudding to clay consistancy, not concrete. Exchanger spec sheet and analysis, as well as tube map are attached.