How to insulate high temp ducting? 1

Status
Not open for further replies.

rstevens

Automotive
Oct 1, 2002
1
I was wondering if someone could direct me to a standard or perhaps send some info my way on the following application:
Installation of a high temperature duct through an exterior wall made of sheet metal cladding.
The duct is 650mm in diameter (OD).
Estimated maximum temp is 400°C.
Sheet metal wall is single sided, has insulation layer w/ reflective surface on inside surface of panel.
The duct centreline is 7.8m above the floor level.

What I need to know is the convention for insulating the duct from the sheet metal such that it does not conduct heat to the wall.

Thanks!
 
Replies continue below

Recommended for you

Put a casing through the wall 4-6 inches larger than your duct. Use High temp insulation to seperate the two pipes. The actual size of the outer casing will depend on the R value of the insulation you choose. What is stopping the heat transfer to the air inside the building?
 