SouthSide08
Electrical
- Apr 4, 2017
- 11
Trying to read up on transferred voltage hazards and cannot seem to understand what the correct solution on this issue. This is similar to thread238-413458. Without using expensive software is there a way to know how to solve the issue.
Typical scenario is an industrial application with the substation say 66kV. we would do calculation of GPR and step and touch voltages but within this substation only. this substation will then feed outdoor process area with 6.9kV motors say 50 feet away which would have a grid of their own. if there is a ground fault at the HV side of the substation how do we prevent or know if there is transferred potential to the process area. is it better to connect the ground grid for these separate areas or should both grid be isolated. or both method can be correct but calculation is needed using software like CDEGS.
Typical scenario is an industrial application with the substation say 66kV. we would do calculation of GPR and step and touch voltages but within this substation only. this substation will then feed outdoor process area with 6.9kV motors say 50 feet away which would have a grid of their own. if there is a ground fault at the HV side of the substation how do we prevent or know if there is transferred potential to the process area. is it better to connect the ground grid for these separate areas or should both grid be isolated. or both method can be correct but calculation is needed using software like CDEGS.