Depending on the length of the opening, the requirement for concealing the lintel, and the wall construction, I have detailed geoff dale's rarely and steve1's more frequently. I have heard of the needle beam procedure, but honestly, it is not done.
If you detail the channels bolted to the wall on either side, the bolts into the wall each end should carry the reaction into the wall, or maybe add steel columns. I like the extra insurance of a bottom plate x the M.O. welded to the channels. This is a great detail for those longer spans. Consider calling for temporary shoring of the floor or roof.
For shorter unexposed spans, I have detailed a sawcut joint each side, with the horizontal legs of steel angles inserted in the joint, extended 8" each end beyond the M.O., and the steel bottom plate added.
By the way, I have never heard of padstones.