Hi all,
I am experiencing an issue with a low-fault current panel X that is connected to an upstream feeder breaker with a capacity of 600V/400A. The client wishes to increase the fault current in the current panel X, but replacing the panel is a challenging task. To resolve the issue, we have decided to add an isolation transformer. My question is whether we should consider the upstream feeder capacity, or just the impedance of the isolation transformer to reduce the fault current in panel X. After checking the connected load for this panel, it is only around 100kW with 600V.
I am experiencing an issue with a low-fault current panel X that is connected to an upstream feeder breaker with a capacity of 600V/400A. The client wishes to increase the fault current in the current panel X, but replacing the panel is a challenging task. To resolve the issue, we have decided to add an isolation transformer. My question is whether we should consider the upstream feeder capacity, or just the impedance of the isolation transformer to reduce the fault current in panel X. After checking the connected load for this panel, it is only around 100kW with 600V.