How we can measure the our FF signa

Status
Not open for further replies.

arslansharif

Industrial
Nov 3, 2017
5
How we can measure the our FF signal .means if i am calibrating a PT honeywell 800 how can i measure my output iscorrexct to the input .e.g in hart if my PT is 0 to 100bar i have give input 50bar i can measure 12mA output and in FF how i can measure with out any communicater e.g hart 475
 
Replies continue below

Recommended for you

I presume the ST800 has no local display.

Buy a local display. Unscrew the screw cover on the PT. Install the display. Configure the display using the LCD transducer function block. Read the values in the display.
 
No i have std 810 which have display i want to measure the output FFwith any standard instrument .
 
Foundation Fieldbus has no analog output. That's why it's called a fieldbus.

I've heard that the communications modules are interchangeable on the ST800. The parts list from the user manual would infer that as well.
ST800_spare_parts_list_HART_hi.jpg


So if you're determined to get an analog HART output from the PT, convert it to HART with a replacement Comm module and terminal block.

If this exercise is to check calibration, using the display on the FF unit is as good a value as you'll get, because the local display shows digital values; the same value FF is providing the host. The ST series local display communicates to the xmtr digitally; the local display is not an analog local meter like the older tan/beige Honeywell's.
 