CivilEngineer401
Civil/Environmental
- Feb 4, 2011
- 24
I am working on a project for a 50 unit apartment building and trying to size the water service. The service is 750-ft long, so due to the length I am concerned about dynamic losses. Since I am not designing a fire flow, I feel that there is no need to be overly conservative and do not want to un-necessarily oversize the pipe. To estimate the peak flow, I started the same way I would estimate peak sewer flows:
50 units x 100 gpd = 5,000 gpd (or 3.5 gpm) multiplied by a peaking factor of 4 = 14 gpm total peak flow for the entire building
I quickly realized that this answer does not make sense since a few showers/sinks on at the same time would surely exceed 14 gpm. I searched online and found the “fixture units method” but the examples online had the peak demand of roughly 20 gpm when you are only looking at 1 house. For one house, I cannot imagine more than 2 sinks and an appliance operating at the same time one which would be roughly 5 gpm.
As an engineer, I started to get quite curios about how to estimate peak water demand. How would you estimate the peak instantaneous water demand be for 5 units, 50 units, 500 units, and 5,000 units?
50 units x 100 gpd = 5,000 gpd (or 3.5 gpm) multiplied by a peaking factor of 4 = 14 gpm total peak flow for the entire building
I quickly realized that this answer does not make sense since a few showers/sinks on at the same time would surely exceed 14 gpm. I searched online and found the “fixture units method” but the examples online had the peak demand of roughly 20 gpm when you are only looking at 1 house. For one house, I cannot imagine more than 2 sinks and an appliance operating at the same time one which would be roughly 5 gpm.
As an engineer, I started to get quite curios about how to estimate peak water demand. How would you estimate the peak instantaneous water demand be for 5 units, 50 units, 500 units, and 5,000 units?