HSS to HSS sleeve connection

Status
Not open for further replies.

NVEIT

Structural
May 19, 2023
2
Does anyone have a reference for how to check an HSS to HSS sleeve connection similar to the attached drawing? I'm working on a TI project where field welding is not allowed within the existing building. The contractor has requested these sleeve connections (made up of 1/4" flat bar fit tight to the specified HSS beam) as a means of erecting these HSS to HSS connections without field welding, but I'm stumped as to how to check this.

Any help is greatly appreciated.
 
 https://files.engineering.com/getfile.aspx?folder=73bce95e-93b8-4605-8e88-ad6a3d0735ac&file=HSS_to_HSS_sleeve_connection.pdf
Replies continue below

Recommended for you

What sort of load? Can you just put a BAR on the underside and connect it with a couple of TEKS3 or TEKS5?

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
It's just supporting a 12psf storefront and a 5psf interior lateral live load.
 
You should easily do that with clip angles, bolts and TEKS 3 or 5. Why sleeve?

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 