fcxdfm
Mechanical
- Apr 19, 2006
- 44
The computer room I am working on is in Houston. The winter outdoor design temperature 20 DB, and 60% RH are used. The space needs to be maintained at 75 +/- 5 Deg. F, and 50% +/- 5% RH throughout the year. The cooling load is about 6 ton and almost 100% sensible load. The outdoor air is about 20% of the total supply. The system is DX unit with 5 KW electric heating, and with hot gas reheat for dehumidity control. The psychrometric chart shows in the winter, the mixed air has 64 DB and 60% RH, about 49 deg. F dew point, before it enters the cooling coil (the room still needs cooling in the winter). However, 49 deg. F dew point is lower than the 55 Deg. F dew point to maintain the space at 75 Deg. and 50% RH. I am confused here - does it mean the space can not be mainted at 75 deg. and 50% RH, and maybe only at 70 Deg. and 49% RH, or 75% deg. and 42% RH? Do I need provide humidifier to keep RH no lower than 45% then?
Thank you very much for help!
Thank you very much for help!