Hi,
I am looking at the fuse characteristic graph for an HV and LV fuse to assess suitable discrimination between the two. I am a bit unsure as to what the impact of changing the voltage ratio of the transformer is when the impedance of the transformer stays the same.
I have attached the graph as an example. If I was looking at 100kVA transformer with 5% impedance and a source fault level of 150MVA. Would the transformer voltage ratio play any role in the discrimination assessment? If system was a 11000/440V versus a 6600/440V? I don't see why it should as the maximum fault level through the transformer should still be the same.
Thanks
I am looking at the fuse characteristic graph for an HV and LV fuse to assess suitable discrimination between the two. I am a bit unsure as to what the impact of changing the voltage ratio of the transformer is when the impedance of the transformer stays the same.
I have attached the graph as an example. If I was looking at 100kVA transformer with 5% impedance and a source fault level of 150MVA. Would the transformer voltage ratio play any role in the discrimination assessment? If system was a 11000/440V versus a 6600/440V? I don't see why it should as the maximum fault level through the transformer should still be the same.