QUESTION: Should a ground grid be designed for a max. circuit breaker de-rated of 63kA for three phase or 75kA for SLG withstand capability?
BACKGROUND:
Ground grid is design is based on ground fault injected into the ground. On the other hand the breaker is limited by the three phase fault & X/R
The following data data have been used to de-rate the circuit breaker withstand short circuit capability.
A) Selected Circuit Breaker Rating:
Interrupting rating current 80 kA rms at Std X/R=17
B) System Parameters
1) Nominal system voltage: 345 kV, 60 Hz.
2) Three-phase fault................ 60 kA & X/R=50.....RESULT: SC detating estimated ~63.kA
3) Single-line-to-ground fault (SLG) 70 kA & X/R=30.....RESULT: SC detating estimated ~75.kA