rockman7892
Electrical
- Apr 7, 2008
- 1,156
I was recently reviewing a concept for a 161kv - 34.5kV Substation that served as a substation for connecting a BESS to the grid. I had some general questions about some of the protection philosophys shown on the one-line sketch that I was hoping to learn from some of the utility folks here what is usually considered the "norm" or "standard".
Attached is one-line sketch I developed showing general protection philosophy with some questions below referencing questions in red on one-line
1) Are PT's with (2) secondry windings that are used for metering and protection typically located on line side of incoming disconnect switch as shown or are there reasons to locate it on the secondary side of switch?
2) Is it typical to see (2) sets of transformer differential relays as shown with one diff zone looking all the way down to secondary of low side feeder breakers and the other looking at ct's on xfmr secondary. I'm not accustomed to seeing (2) relays and typically are used to seeing on xfmr diff that only looks to CT's on secondary of transformer. Is it typically to have (2) for redundancy or a specific needs for the (2) zones?
3) Currently I only shows xfmr neutral CT's connected to one of xfmr differential relays? Is there a need to connection another set of CT's on each neutral to connect to the second diff relay?
4) I shows a feeder protection relay (SEL-751) on high side of breaker. I usually see this relay in this application but was never quite sure of the reasoning considering both the xfmr diff relays are capable of providing many of the same functions with high side CT's (50/51, etc...). Is there usually a specific need to including a feeder protection relay here (perhaps use for BF,etc..?)
5) One-Line shows (2) different line differential relays which will have fiber connection to upstream substation. Is it typically to see (2) different line differential relays in this application? Is one simply a redundant backup?
6) Is there typically a need to have a feeder relay on the secondary of the transformer? I would think not again considering that the xfmr relay with secondary CT's provides many of the same functions as this secondary feeder relay would. Is there a need if certain number of radial feeders is exceeded?
7) The feeders from the 34.5kV collector bus will feed down to large BESS units. I know that some inverters associated with BESS systems have ability to act in "grid forming" mode with capability to operate in islanded mode. If this is the case is there a need to perform sync check functions across feeder breakers when re-syncing to grid after a loss of utility?
Appreciate the help or any other comments anyone has.
Attached is one-line sketch I developed showing general protection philosophy with some questions below referencing questions in red on one-line
1) Are PT's with (2) secondry windings that are used for metering and protection typically located on line side of incoming disconnect switch as shown or are there reasons to locate it on the secondary side of switch?
2) Is it typical to see (2) sets of transformer differential relays as shown with one diff zone looking all the way down to secondary of low side feeder breakers and the other looking at ct's on xfmr secondary. I'm not accustomed to seeing (2) relays and typically are used to seeing on xfmr diff that only looks to CT's on secondary of transformer. Is it typically to have (2) for redundancy or a specific needs for the (2) zones?
3) Currently I only shows xfmr neutral CT's connected to one of xfmr differential relays? Is there a need to connection another set of CT's on each neutral to connect to the second diff relay?
4) I shows a feeder protection relay (SEL-751) on high side of breaker. I usually see this relay in this application but was never quite sure of the reasoning considering both the xfmr diff relays are capable of providing many of the same functions with high side CT's (50/51, etc...). Is there usually a specific need to including a feeder protection relay here (perhaps use for BF,etc..?)
5) One-Line shows (2) different line differential relays which will have fiber connection to upstream substation. Is it typically to see (2) different line differential relays in this application? Is one simply a redundant backup?
6) Is there typically a need to have a feeder relay on the secondary of the transformer? I would think not again considering that the xfmr relay with secondary CT's provides many of the same functions as this secondary feeder relay would. Is there a need if certain number of radial feeders is exceeded?
7) The feeders from the 34.5kV collector bus will feed down to large BESS units. I know that some inverters associated with BESS systems have ability to act in "grid forming" mode with capability to operate in islanded mode. If this is the case is there a need to perform sync check functions across feeder breakers when re-syncing to grid after a loss of utility?
Appreciate the help or any other comments anyone has.