cjw99
Structural
- Jan 26, 2009
- 4
I am designing the lateral bracing system for a rectangular building (approx. 200'x 160'x 40' tall). Seismic deisgn does not apply for this building. The roof has a 90'x90'x 8' tall U-shaped screen wall around the hvac units (no roof over the units). My coworkers and I are debating the proper wind load to apply to the screen walls.
Typically our engineers are applying the combined windward + leeward parapet wind pressures to each of the screen walls. My combined parapet wind pressure is 47psf (28.8psf windward + 18.2psf leeward). Under this methodology, I need to add 33.8 kips (47psf x90'x8')of wind load in the direction with 1 wall and an 67.7 kips (47psf x90'x8'x2) of wind load in the direction with 2 walls to account for the screen.
This seems very conservative to me. How are other engineers approaching this situation? If you disagree, can someone point out a code reference that would lead to using a reduced load. Thanks.
Typically our engineers are applying the combined windward + leeward parapet wind pressures to each of the screen walls. My combined parapet wind pressure is 47psf (28.8psf windward + 18.2psf leeward). Under this methodology, I need to add 33.8 kips (47psf x90'x8')of wind load in the direction with 1 wall and an 67.7 kips (47psf x90'x8'x2) of wind load in the direction with 2 walls to account for the screen.
This seems very conservative to me. How are other engineers approaching this situation? If you disagree, can someone point out a code reference that would lead to using a reduced load. Thanks.