I posted this in the wrong forum before. Perhaps a mod can delete the previous one?
I'm trying to size a cooler based on actual heat created in a system. In a closed loop circuit, do I consider leakage from the charge pump (10-15% of charge flow * charge setting), leakage through the pump case (10-15% of max flow * Delta P), and leakage through the motor case (10-15% of max flow * Delta P)? Just want to make sure I'm not doubling up on the pump and motor case.
For Delta P in the pump and motor case I am using (pressure setting - charge setting). I am running two cases to determine worst case -- high speed, low pressure and low speed, high pressure. HP of the prime mover limits high speed, high pressure instance.
Comments?
I'm trying to size a cooler based on actual heat created in a system. In a closed loop circuit, do I consider leakage from the charge pump (10-15% of charge flow * charge setting), leakage through the pump case (10-15% of max flow * Delta P), and leakage through the motor case (10-15% of max flow * Delta P)? Just want to make sure I'm not doubling up on the pump and motor case.