I've got a unique situation with a recently re-stacked hydrogenerator. Vitals are:
# poles = 56 ; # stator slots = 360 ; line freq = 60 Hz ; rpm = 128.57
Old design had 4 stator core splits ; New design uses a continuous core stack
Vibration taken directly from the back of the core iron shows a 4.3 g-pk component at 720 Hz, with the next largest response at its first harmonic of 1440 Hz at 0.45 g. The adjacent keybar showed similar but slightly higher radial responses of 4.8 and 0.9 g-pk, respectively. Tangential responses on the keybar were 0.9 and 2.4 g, respectively.
Through each spectrum 120 Hz harmonics are present, but they are comparatively low level, typically 0.05 to 0.09 g.
The 720 Hz vibration creates significant audible noise, with levels that increase directly with load. At FSNL and with excitation on, we have about 75 dbA at 20' outside the generator enclosure. At 35MW load, we have 90+dB, with the predominant 720 Hz component.
Sister units to this problem unit operate at full load with noise levels in the 75 dBA range; no access for vibration measurements at this point. Our client is not accepting the unit for operation based upon the noise being generated. We have had several theories regarding the source of the noise, with possible solutions.
Since I'm an ME, my working knowledge of generator circuitry is limited. I'd like to get some feed back from the EE's out there if they feel there is anything in either the static excitation circuitry or the generation circuitry that would cause this.
It has been suggested that the static excitation frequency would be at 6x-Line, or 360 Hz, and that 720 Hz would also be present. However, the 720 Hz vibration and noise DOMINATE the response spectra.
We are also wondering about the 2x-Line harmonics. Do they suggest stator core looseness, or should they be expected?
I would appreciate any commentary on the issue.
Thanks,
Stan
# poles = 56 ; # stator slots = 360 ; line freq = 60 Hz ; rpm = 128.57
Old design had 4 stator core splits ; New design uses a continuous core stack
Vibration taken directly from the back of the core iron shows a 4.3 g-pk component at 720 Hz, with the next largest response at its first harmonic of 1440 Hz at 0.45 g. The adjacent keybar showed similar but slightly higher radial responses of 4.8 and 0.9 g-pk, respectively. Tangential responses on the keybar were 0.9 and 2.4 g, respectively.
Through each spectrum 120 Hz harmonics are present, but they are comparatively low level, typically 0.05 to 0.09 g.
The 720 Hz vibration creates significant audible noise, with levels that increase directly with load. At FSNL and with excitation on, we have about 75 dbA at 20' outside the generator enclosure. At 35MW load, we have 90+dB, with the predominant 720 Hz component.
Sister units to this problem unit operate at full load with noise levels in the 75 dBA range; no access for vibration measurements at this point. Our client is not accepting the unit for operation based upon the noise being generated. We have had several theories regarding the source of the noise, with possible solutions.
Since I'm an ME, my working knowledge of generator circuitry is limited. I'd like to get some feed back from the EE's out there if they feel there is anything in either the static excitation circuitry or the generation circuitry that would cause this.
It has been suggested that the static excitation frequency would be at 6x-Line, or 360 Hz, and that 720 Hz would also be present. However, the 720 Hz vibration and noise DOMINATE the response spectra.
We are also wondering about the 2x-Line harmonics. Do they suggest stator core looseness, or should they be expected?
I would appreciate any commentary on the issue.
Thanks,
Stan