Hydronic system fill PRV setting?

Status
Not open for further replies.

Takket3

Mechanical
Joined
Apr 28, 2016
Messages
21
Location
US
I know from the following that a PRV should be set to maintain 4PSI at the top of the system for "positive venting".


But what if the PRV is actually at the top of the system? (Same elevation as my chilled water piping). Do i just set it at 4PSI? Or should I use a minimum of some other pressure?
 
You should set it so that you don't exceed the design pressure of your system at the lowest point. It would be better to set it higher than 4 psig. You always need to allow some margin from normal/max operating and relief pressures.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
In addition to the PRV on the water makeup line set to maintain minimum 4 psig above the highest piping static water level pressure provide a relief valve vented to floor drain that would open before the maximum allowable water pressure in the system is reached if the water makeup PRV fail open.
 