cespi82
Materials
- Dec 23, 2009
- 36
Hi Gents,
I have to hydrotest the tubes of a Fin Fan Cooler and what came first to my mind was the API-510 criterion of 1.3 x MAWP x the Correction for Temperature (S Test Tem / S Des Temp).
The equipment has 5 years in service and 8 of its tubes have leaked. We have plugged the tubes out and now what is next is the hydrotest of the whole thing. Does the MAWP has to be recalculated per code as the equipment has several years in service and thickness values are not obviously the same as the initial stage?
No wall thickness data is available at this moment. If effectively the MAWP requires per code to be recalculated, should we make the effort to conduct and IRIS or similar technique in order to have thickness data and recalculate the MAWP?
How big it would be the mistake (if it is mistake) if we just hydrotest the equipment at the MAWP written on the plate?
Kind regards,
Cesar
I have to hydrotest the tubes of a Fin Fan Cooler and what came first to my mind was the API-510 criterion of 1.3 x MAWP x the Correction for Temperature (S Test Tem / S Des Temp).
The equipment has 5 years in service and 8 of its tubes have leaked. We have plugged the tubes out and now what is next is the hydrotest of the whole thing. Does the MAWP has to be recalculated per code as the equipment has several years in service and thickness values are not obviously the same as the initial stage?
No wall thickness data is available at this moment. If effectively the MAWP requires per code to be recalculated, should we make the effort to conduct and IRIS or similar technique in order to have thickness data and recalculate the MAWP?
How big it would be the mistake (if it is mistake) if we just hydrotest the equipment at the MAWP written on the plate?
Kind regards,
Cesar