Lutfi
Structural
- Oct 20, 2002
- 1,032
I am being consulted on some DTI (Direct Tension Indicators) that were installed as follows:
1. ¾ inch diameter A325, for slip critical joints, contractor used DTI
2. Contractor installed DTI under nut which is not the best application
3. Contractor did not use a hardened washer between DTI and nut (turning element)
4. Contractor asked DTI manufacturer to duplicate the filed condition using Skidmore tool
5. Test results from six (6) bolts indicated that only at tension of 34 kips; the feeler gage had refusals to qualify proper tension
Does any one have words of wisdom? There are many bolts that already installed. Your quick response would be greatly appreciated.
Good night
1. ¾ inch diameter A325, for slip critical joints, contractor used DTI
2. Contractor installed DTI under nut which is not the best application
3. Contractor did not use a hardened washer between DTI and nut (turning element)
4. Contractor asked DTI manufacturer to duplicate the filed condition using Skidmore tool
5. Test results from six (6) bolts indicated that only at tension of 34 kips; the feeler gage had refusals to qualify proper tension
Does any one have words of wisdom? There are many bolts that already installed. Your quick response would be greatly appreciated.
Good night