I/O Fault table 1

Status
Not open for further replies.

TransD

Electrical
May 15, 2011
21
US
I have heard that service request 15 will allow me to log the last PLC I/O fault into a register. I am using Proficy 6.0 Does anyone have any suggestions for implementing service request 15? Thanks.
 
Replies continue below

Recommended for you

Run Service Request 15 when %SA3 comes high, that is any Application Fault, or %SA23, an I/O module fault. Search PME's online help for more "System Variables" for more fault bits.
 
Thanks. This is a GE Fanuc 90-70 PLC with genius blocks. Thanks for any help from anyone.
 